Originally Posted by
SandMike
I note that your photo doesn't show the copper bars linking the RCCD & the MCB's that the diagram shows - you were given these by the shop weren't you ??
I have 1 copper bar, but it only links the live from the RCD to the Mini Circuit Breakers (as shown in the diagram). On this subject, for the other connections within the unit, like from the connection from the Main Circuit Breaker to the RCD (both live and neutral), the connection from the neutral screw-in bar to the RCD, and the neutral connection from the Main Circuit Breaker to the Ground screw-in bar, what size wire should I be using? From the mini circuit breakers to the appliances I'm using either 1.5mm or 2.5mm sized wiring.
HINO's guide recommends the ground wire to the ground rod should be 4mm minimum. My girlfriend's house only has a 5amp meter, but I don't want to have to change the internal wiring of the consumer unit should we upgrade to a larger meter. The Main Circuit Breaker and RCD I purchased were the 40amp variety (the price was the same and I figured it would give us future room for expansion). Can I please get a little more guidance on the wire size I should be using for the internal connections within the circuit breaker.
Matt it sounds to me like the load you have on this 5 amp supply is way too much. Someone "very" qualified needs to review this installation as you mentioned a water heater plus lighting and other appliances. The whole house needs a higher amp meter and supply based on your description. The size of the earth cable to the copper rod needs to be sized to at least the same as the heaviest supply conductor from the pole. But a minimum of 4 mm. Connecting a MEN link can be more dangerous if the other PEA connections on this supply are not using a MEN link. Do not use the MEN link unless you can be sure the entire area uses the MEN system.
Thanks SandMike for your help, and thanks HINO, I've read almost that whole website.
--matt